Stability
GATE Electrical Engineering · 29 questions across 19 years (1993-2022) · 48% recurrence rate
Recurrence sparkline
1993–2022Difficulty mix
Question types
All 29 questions on Stability
A 20 MVA, 11.2 kV, 4-pole, 50 Hz alternator has an inertia constant of 15 MJ/MVA. If the input and output powers of the alternator are 15 MW and 10 MW, respectively, the angular acceleration in mechanical degree/s 2 is _...
Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Ass...
Consider a lossy transmission line with V 1 and V 2 as the sending and receiving end voltages, respectively. Z and X are the series impedance and reactance of the line, respectively. The steady-state stability limit for...
A 3-phase, 2-pole, 50 Hz, synchronous generator has a rating of 250 MVA, 0.8 pf lagging. The kinetic energy of the machine at synchronous speed is 1000 MJ. The machine is running steadily at synchronous speed and deliver...
A 50 Hz generating unit has H-constant of 2 MJ/MVA. The machine is initially operating in steady state at synchronous speed, and producing 1 pu of real power. The initial value of the rotor angle $$\delta $$ is $${5^ \ci...
The angle $$\delta $$ in the swing equation of a synchronous generator is the
A cylindrical rotor generator delivers $$0.5$$ pu power in the steady-state to an infinite bus through a transmission line of reactance $$0.5$$ pu. The generator no-load voltage is $$1.5$$ pu and the infinite bus voltage...
A $$500$$ $$MW,$$ $$21$$ $$kV,$$ $$50$$ $$Hz,$$ $$3$$-phase, $$2$$-pole synchronous generator having a rated $$p.f.=$$$$0.9,$$ has a moment of inertia $$\,\,27.5\,\, \times \,\,{10^3}\,\,kg\,\,{m^2}.\,\,$$ The inertia co...
A generator feeds power to an infinite bus through a double circuit transmission line. A $$3$$ phase fault occurs at the middle point of one of the lines. The infinite bus voltage is $$1$$ pu, the transient internal volt...
A generator feeds power to an infinite bus through a double circuit transmission line. A 3 phase fault occurs at the middle point of one of the lines. The infinite bus voltage is 1 pu, the transient internal voltage of t...
A 50 Hz, 4-pole, 500 MVA, 22 kV turbo-generator is delivering rated megavolt-amperes at 0.8 power factor. Suddenly a fault occurs reducing is electric power output by 40%. Neglect losses and assume constant power input t...
A generator delivers power of 1.0 p.u. to an infinite bus through a purely reactive network. The maximum power that could be delivered by the generator is 2.0 p.u. A three-phase fault occurs at the terminals of the gener...
A round rotor generator with internal voltage $${E_1} = 2.0\,\,$$ p.u.and $$\,X = 1.1\,\,$$ p.u. is connected to a round rotor synchronous motor with internal voltage $$\,\,{E_2} = 1.3\,\,$$ p.u. and $$\,X = 1.2\,\,$$ p....
Consider a power system with three identical generators. The transmission losses are negligible. One generator ($$G1$$) has a speed governor which maintains its speed constant at the rated value, while the other generato...
A transmission line has a total series reactance of 0.2 pu. Reactive power compensation is applied at the midpoint of the line and it is controlled such that the midpoint voltage of the transmission line is always mainta...
A power system has two synchronous generators. The Governor-turbine characteristics corresponding to the generators are P 1 = 50(50 – f), P 2 = 100 (51 – f) Where f denotes the system frequency in Hz, and P 1 and P 2 are...
A synchronous generator is connected to an infinite bus through a lossless double circuit transmission line. The generator is delivering 1.0 per unit power at a load angle of $${30^0}$$ when a sudden fault reduces the pe...
A transmission line has equal voltages at the two ends, maintained constant by two sources. A third source is to be provided to maintain constant voltage (equal to end voltages) at either the midpoint of the line or at $...
A synchronous generator, having a reactance of 0.15 p.u., is connected to an infinite bus through two identical parallel transmission lines having reactance of 0.3 p.u. each. In steady state, the generator is delivering...
Steady state stability of a power system is the ability of the power system to
The load carrying capability of a long AC transmission line is
Series capacitive compensation in $$EHV$$ transmission lines is used to
A power station consists of two synchronous generators A and B of ratings 250 MVA and 500 MVA with inertia constant 1.6 p.u. and 1.0 p.u., respectively on their own base MVA ratings. The equivalent p.u. inertia constant...
A synchronous motor is receiving 50% of the power it is cable to receiving from an infinite bus. If the load on the motor is suddenly reduced to 80% of the previous value, swing of the motor around is new equilibrium pos...
The use of high-speed of circuit-breakers
A $$100$$ $$MVA$$, $$11$$ $$kV$$, $$3$$-phase, $$50$$ $$Hz$$, $$8$$-pole synchronous generator has an inertia constant H equal to $$4$$ $$MJ/MVA.$$ The stored energy in the rotor of the generator at synchronous speed wil...
During a disturbance on synchronous machine, the rotor swings from A to B before finally settling down to a steady state at a point C on the power angle curve. The speed of the machine during oscillation is synchronous a...
In a system, there are two generators operating in parallel. One generator, of rating 250 MVA, has an inertia-constant of 6 MJ/MVA while the other generator of 150 MVA has an inertia-constant of 4 MJ/MVA. The inertia-con...
The transient stability of the power system can be effectively improved by